Electrical EngineeringVery hard
An open-circuit test on a transformer (LV side) gives 400 V, 1 A, 300 W. The magnetising reactance Xm referred to the LV side is
- A. 533.33 Ω
- B. 400 Ω
- C. 228.57 Ω
- D. 604.74 Ω
Correct answer: D. 604.74 Ω
Iw = W/V = 0.7500 A; Im = √(I²-Iw²) = 0.6614 A; Xm = V/Im = 604.74 Ω.
Practise more Electrical Machines (Electrical) questionsElectrical Machines (Electrical): notes and key points