Electrical EngineeringModerate
A plant has a maximum demand of 50 MW and supplies 1.8 x 10^8 kWh in a year (8760 h). The load factor is about
- A. 41%
- B. 80%
- C. 20%
- D. 100%
Correct answer: A. 41%
Average load = 1.8e8 / 8760 = 20,548 kW; LF = 20.55 / 50 = 0.411.
Practise more Power Systems & Protection (Electrical) questionsPower Systems & Protection (Electrical): notes and key points
More Power Systems & Protection (Electrical) questions
- A 100 MVA base is chosen. A generator of 50 MVA with 0.2 pu reactance on its own base has a reactance on the 100 MVA base of
- A short 3-phase line (total R = 1.63 Ω, X = 5.45 Ω per phase) delivers 20 MW at 33 kV (line) and 0.85 pf lagging. The percentage voltage…
- A 3-phase line of resistance 12.1 Ω per phase delivers 20 MW at 110 kV and 0.95 pf. The transmission efficiency (considering only the line…
- A transmission line loses 6 MW when delivering a fixed load at unity pf at 66 kV. If the transmission voltage is raised to 132 kV for the…
- A medium transmission line (nominal-π, resistance neglected) has total series reactance 100 Ω and total shunt susceptance 1000 µS. With…
- A medium transmission line (nominal-π, resistance neglected) has total series reactance 150 Ω and total shunt susceptance 600 µS. With 400…