Electrical EngineeringModerate
A 100 MVA base is chosen. A generator of 50 MVA with 0.2 pu reactance on its own base has a reactance on the 100 MVA base of
- A. 0.1 pu
- B. 0.4 pu
- C. 0.2 pu
- D. 0.8 pu
Correct answer: B. 0.4 pu
X_new = 0.2 x 100 / 50 = 0.4 pu (same voltage base).