Electrical EngineeringHard
A 50 Hz single-phase transformer has 300 primary turns on a 2200 V (rms) supply. The maximum core flux is
- A. 23.343 mWb
- B. 1651.652 mWb
- C. 36.667 mWb
- D. 33.033 mWb
Correct answer: D. 33.033 mWb
Φm = V1/(4.44 f N1) = 2200/(4.44×50×300) = 33.033 mWb.
Practise more Electrical Machines (Electrical) questionsElectrical Machines (Electrical): notes and key points
More Electrical Machines (Electrical) questions
- A single-phase, 50 Hz, 3300/220 V transformer has a maximum core flux of 50 mWb. The number of secondary turns is approximately
- A transformer has percentage resistance 1% and leakage reactance 8% at full load. Using the approximate formula, the voltage regulation at…
- A 100 kVA transformer with iron loss 1000 W and full-load copper loss 3200 W delivers load at 0.9 pf. Its maximum efficiency is
- A 500 kVA transformer with iron loss 1000 W and full-load copper loss 6000 W delivers load at 1 pf. Its maximum efficiency is
- An open-circuit test on a transformer (LV side) gives 220 V, 4 A, 100 W. The magnetising reactance Xm referred to the LV side is
- An open-circuit test on a transformer (LV side) gives 400 V, 1 A, 300 W. The magnetising reactance Xm referred to the LV side is