Electrical EngineeringVery hard
A transformer has percentage resistance 1% and leakage reactance 8% at full load. Using the approximate formula, the voltage regulation at full load, 0.9 pf leading, is
- A. 8.1 %
- B. -2.587 %
- C. 4.387 %
- D. 9 %
Correct answer: B. -2.587 %
Reg = εr cosφ - εx sinφ = 1×0.9 - 8×0.4359 = -2.587 %.