Electrical EngineeringHard
A single-phase, 50 Hz, 3300/220 V transformer has a maximum core flux of 50 mWb. The number of secondary turns is approximately
- A. 991
- B. 40
- C. 297
- D. 20
Correct answer: D. 20
N2 = V2/(4.44 f Φm) = 220/(4.44×50×0.05) = 19.8 turns.